potential transformer class
hi
i need to know whats the meaning of class ( 6p ) that i found in the name plate of a potential transformer of two secondary windings ( first coil class is 0.5 ) and the pt is made in China.
where could i find any detailed information about this please
thank you
RE: potential transformer class
It is an IEC-rating
See:
http://www.areva-td.com/static/html/TDE-AGF_Product-Product_Detail2_1089880316992.html?&famid=1107432285135&;typid=1107432285131&productline=1079943326752
Download chapter 6 (Current and voltage transformers)
Table 6.1 for the limits of measuring VTs
Table 6.2 for the limits of protective VTs
or refer to the IEC-standard:
IEC60044-2
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376
The first coil/core (0.5 class) of your PT is for metering pupose, and the second one, 6p, is for protection (residual voltage /open delta) purpose.
The standard accuracy classes for protective voltage transformers are 3p and 6p.
First letter indicates %voltage (ratio) error and phase displacement error.
As per IEC-44-2, the voltage error and the phase displacement error at rated frequency shall not exceed followong values at 5% of rated voltage.
at 2 % of rated value, the limits of error & phase dsplacement (with burdens of between 25%-100%) will be twice as high as those given below.
Accuracy class     % voltage errot  Ph displacement error.
3P                         3            120min or 2deg
6p                         6            240min or 4deg
Srinivas
Hi bjeservice,
It's an excellent link, given by Mr Ralph.
Thanks to Mr RalphChristie.