Cable selection

Cable selection

Cable selection

(OP)
I need to supply a three-phase transformer that has a peak/starting power of 7kVA. Voltage supply im my country is 230V. If my calculations are correct, the starting current on each phase is 8.2A and I selected a 5*2.5mmm2 cable with a 3*10A fuse. Will that be ok? Thanks!

RE: Cable selection

What u doing bro:
It is a 3 Ph transformer
that means =Sqrt(3)* V*I= 7000 VA
now I(Line)=17.59 A
 and check the electrical code rules, if it is in a conduit or open , for this much current carrying capacity what cable size do u need and u need a fuse of a capacity of 25 % higher capacity.
got it.
Let me know if still problem exists.

RE: Cable selection

curlis19 calculation is corect if 230V is the line-to-line voltage. But if 230V is the phase voltage, line-to-line voltage will be 400V and the current (I) will be 10.1A i.e. 7000/(sqrt(3)/400).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources