Implications of using larger motor starter?

Implications of using larger motor starter?

Implications of using larger motor starter?

(OP)
Is there anything inherently wrong with using a motor starter that is larger than required? For example, say a 1hp motor requires a 00 starter, but I have an extra size 1 starter laying around. Assuming I use the correct thermal elements sized according to the 1hp motor, I imagine it would work fine, but is this considered bad practice or prohibited  by code?

RE: Implications of using larger motor starter?

Absolutely nothing.  Assuming that you can find
the correct heaters :)
<als>

RE: Implications of using larger motor starter?

Aslo pay attention to the Short Circuit Protective Device (SCPD) in the starter. If it is fses, just replace them with the size appropriate for your load. If it is a circuit breaker, it may need to be changed because the lowest settings may be too high for that motor.

"Our virtues and our failings are inseparable, like force and matter. When they separate, man is no more." Nikola Tesla
Read the Eng-Tips Site Policies at FAQ731-376  
Member, P3

RE: Implications of using larger motor starter?

As far as you adjust the overload and short circuit protection properly, it will work and probably last for many more years than the specified size, cost is the difference.

RE: Implications of using larger motor starter?

If we extend this discussion to DC contactors, using an oversized contactor can have a detrimental effect if the contactor employs a magnetic blow-out on the poles. These contactors use the magnetic field generated by the load current to help break the arc - if the contactor is hugely oversized then the magnetic field generated by the current is weaker than the contactor was designed for and the arc extinguishing capability of the pole is reduced.

----------------------------------

One day my ship will come in.
But with my luck, I'll be at the airport!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources