AC Drive Load Acceleration
Does anyone know of a source for methodology to calculate motor acceleration by a drive. The load torque will vary from standstill to full rpm, so that seems to eliminate the formulae in the Nema application guide, for a more exact calculation.
My first thought was that with a frequency ramp, for each small step, a frequency perturbation would need to be applied to the motor to calculate motor speed change dynamics.
RE: AC Drive Load Acceleration
T = J * dw/dt
where
T = accelerating torque = Motor Torque minus Load torque
J = rotating inertai
w = radian rotational frequency = 2*pi*f
f = rotational frequency (rotations / second)
Rearrange
w(t) = (1/J) integral (T) dt
You can do a numerical integration with motor torque a function of both time (ramping changes torque speed curve over time) and speed (where are you on the torque speed curve) and pump torque a function of speed only.
I'm not sure if this is what you're looking for.
With a linear acceleration ramp, the drive will attempt to apply a constant accelerating torque.
Attempted Accel Torque = Wk^2 X (RPM/time)/308 for any incremental speed change
Since the ramp is linear, RPM/time is (ramp time) / (total speed change)
The available accel torque is drive torque capacity minus the load's steady-speed torque requirement
If, at any speed, attempted accel torque is less than available accel torque, the drive will go into current limit or shut down
A good drive should be capable of accelerating at constant torque in current limit. While in current limit, the incremental speed change will be given by:
RPM change = (308 X time increment) / Wk^2
RPM change = Torque X (308 X time increment) / Wk^2
RPM change = (Torque X 308 X time increment) / Wk^2
In a small step of frequency and voltage (V/f = constant), these should change immediately, but the rotor speed will take time, so it would seem that the rotor slip frequency also changes immediately.
Any rotating system obeys the laws of physics. It does not mater if you have a variable frequency drive or not.
As Electricpete stated the basic relation is:
dw/dt = T/j
When a VFD is used, ti (the time allowed in each step, before the frequency is increased ) must be large enough to allow acceleration to full speed of the system inertia (j). That will give the time extent of the accelerating ramp.
Note that the formula given by CJCPE is a particular case when the units are; Torque in Lb-ft, speed in rpm,constant of inertia in Lbf-Ft^2 and time in sec.
But is there a way the drive can know the rotor speed, other than direct measurement?