Overhead Lines

Overhead Lines

Overhead Lines

(OP)
I am in the process of reruiting a number of 4160 distribution lines.  I am finding it difficult to locate the current rating of various ACSR conductors.  If someone could point me in the right direction it would be appreciated.  Also, what is the usual acceptable temperature rise in overhead lines, and where could one find a set of tables with various ampacity vs maximum temperature?

RE: Overhead Lines

See the enclose site from SKM republishing the table from the Westinghouse T&D Book.

RE: Overhead Lines

(OP)
Thanks for the tables.  Is there any recommendation as to weither to use 75C or 90C, and either simple conversion to change from one rating to another?

RE: Overhead Lines

Ranger
One thing to consider is that at the 90C rating, you will have greater sag in the conductor so you need to design that in to you job.

RE: Overhead Lines

Infrared thermography is commonly used for this application but is not especially accurate. There may be some good uses in diagnostics, maybe more for connections than the conductor itself.

RE: Overhead Lines

The maximum temperature is generally limited by sag and clearance considerations.  Many utilities use 75 deg C because this is what the Westinghouse T&D Handbook uses and was the basis for NESC basic clearances.  The annealing temperature of ACSR is much higher, however, so you can use higher temperatures if you account for it in providing clearances.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources