I have a customer that has a substation that they want the gravel replaced.  Is there a IEEE Std for this work?  If so ehat is it?

RE: Substation Grading

IEEE Std 80 deal with surfacing material resistivity to maintain the allowable step and touch potential at desirable level as a function of the resistivity and thickness of a crushed stone layer .

From the civil engineering standpoint, crushed rock may be use as soil stabilizer, internal roadway, sub drainage, etc.

Crushed stone # 2 without fines material is expected to have a wet resistivity around 2000 to 3000 Ohm-meter. A layer of 4 inches inside the substation and 3 ft beyond the fence usually provide may have good results.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources