Megger testing procedures
3

Megger testing procedures

Megger testing procedures

(OP)
Hi,

I've been asked to find an IEEE or equivalent test procedure for meggering from the T-leads in an MCC cubicle to the motor in the field.  Any help would be much appreciated.

Ben

RE: Megger testing procedures

What is the operating voltage of your cables?

Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants

RE: Megger testing procedures

NFPA 70E should help you also
.
.
.
.

Start each day off with a smile
,,, then you've at least that much out of the way!

RE: Megger testing procedures

I think you meant to say NFPA 70B

Scott Peterson
Training Manager
Power Plus Engineering
www.epowerplus.com

RE: Megger testing procedures

This is what I refer to when asked. There may be changes (Rev's) but pretty standard for Rotating Equipment and Cables. Corrections welcome.

IEEE STANDARD 43-1974 (29) ACCEPTANCE CRITERION FOR INSULATION
For Rotating Equipment  
•IR is equal to or greater than 1 Megohm plus rated equipment KV.

MEGGER

IEE STANDARD NO. 43.1974
ACCEPTANCE CRITERION:
•IR IS EQUAL TO OR GREATER THAN 1 MEGOHM + RATED KV.
    
MOTOR RATING VOLTAGE    DC MEGOHMETER (Test Voltage)
460/575                                500 or 1000
2300/2400                             1000 or 2500
4000/41602                            2500
6600/6900                              5000
            
POLARIZATION INDEX

PI = IR Measurement at 10 minutes
     (Divided by)IR Measurement at 1 minute

ACCEPTANCE CRITERION:
Usually 2

IEEE STANDARDS: 690-1984(1), 422-1986(43), 43-1974 (29)
(for cable Insulation testing)

RE: Megger testing procedures

Again,  I do not completely understand the application.  However, I will give a warning that the IEEE standards noted are not applicable for shielded MV cables with extruded insulation. Per IEEE 400-2001 DC should not be used as it can damage aged cable and will not detect most defects.  I recommend at least a AC withstand or, better yet, a PD stress test.  Let me know if you have any questions.

Kind regards,

-Ben

Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants

RE: Megger testing procedures

Most of the regs that I deal with is 2 X operating voltage + 100v

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources