×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

IEC question

IEC question

IEC question

(OP)
Can anyone tell me what the minimum tripping voltage in % of nominal is for a DC powered circuit breaker in IEC territory? Thanks.

RE: IEC question

85% for closing and 70% for tripping.  

RE: IEC question

(OP)
Thanks. And relays can shut down below 80%? The IEEE C37.90 working group claims their 80% value is in line with IEC. One explanation offered for the difference from relay to breaker is the voltage drop from the relay near the battery in the control building to the breaker in the yard. But sometimes relays are in the breaker cabinet..? Anyone have some more insight on this?

RE: IEC question

The present day numerical relays accept very wide range for DC voltage supply.

With regard to a low figure of 70% for breaker trip coil, it occurs only at the time of picking up of the breaker trip coil and is understandable considering huge magnitude of current that the trip solenoid would draw.

Typically a breaker trip coil burden would be 200W as against a couple of watts (at the most) of a protection relay.

It may also be noted that the high speed, high impedance trip relays like type MVAJH of Areva are designed to pick up and close the trip contacts positively even at 50% of rated DC voltage.

RE: IEC question

(OP)
Of course the time of tripping is right when you don't want your relay crapping out. Even if the trip itself is successful, relay may still weld its contacts trying to interrupt the trip current before the aux switch does.
 
Unless a separate circuit is pulled for the relay, a relay installed at the breaker will see the full voltage drop. When retrofitting a microprocessor relay into a breaker cabinet that had electromechanical relays for example.

ANSI breakers are required to trip down to about 56% nominal. Sounds to me like the last gasp of a dying battery. But the relay is out at 80%.

Areva's 50% sounds a lot more reasonable. Shouldn't be that big a deal anymore with the wide ranging power supplies available.

Any input from the manufacturers? Is Davidbeach listening?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources