Fusing a Zig-Zag transformer

Fusing a Zig-Zag transformer

Fusing a Zig-Zag transformer

(OP)
Looking to install a 4160 volt system dedicated to a 3000 HP motor.  Total cable length is less than 200 feet.  Existing transformer secondary is delta connected.  Contractor wants to install a resistance grounded (15 ampere limit) using a zig-zag grounding transformer.  Question:  Do you fuse the zig-zag?  Second question - if you used a wye-delta grounding transformer instead of a zig-zag, would you fuse it?
Personal preference - due to the criticality of the load, I would go ungrounded with a ground detection scheme to alert on a ground fault, but maybe I am old-fashioned.
Regards,
Raisinbran

RE: Fusing a Zig-Zag transformer

If you must meet NEC, see Article 450.5.  I would fuse it just to protect against unlikely case of an internal fault - either zig-zag or delta-wye.  

You're better off with the high-resistance grounding instead of ungrounded due to reduced overvoltage risks.  But 15 amps sounds high - the current is normally limited to roughly the capacitive charging current in high resistance grounding - this is usually less than 5 amps.

The delta-wye unit will work just fine for grounding and will probably be a lot easier to come by - probably cheaper as well.  Since you are resistance grounding, you don't need a very large unit.  

RE: Fusing a Zig-Zag transformer

According to my opinion it would depend on if the zig-zag/delta-wye transformer is included in a protective zone, like in a differential or REF zone. If not, I would fuse it. I am not familiar with the NEC, so I would not/can not comment on it.

It seems as if it is difficult to obtain zig-zag transformers in certain parts of the world - and it would be most probably a special order to obtain one. If it is true in your case, I would go for a delta-wye unit. However, a zig-zag trsf is usually smaller compared to the same size delta-wye units.

Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon

Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376

RE: Fusing a Zig-Zag transformer

Per NEC 450.5 (B) (2) the zig-zag autotransformer must be protected by a device that will open simultaneously all ungrounded conductors. The setting of the device cannot exceed 125% of the rating of the autotransformer's continuous rating. Therefore, a simple fused disconnect (no anti-single phasing protection) can not be used.

The NEC seems to be silent on the use of a wye delta grounding transformer, probably because the autotransformer installation is cheaper.  I would recommend in this case following the same rules that apply to the grounding autotransformer.

It is interested to note that if you were to make this a 3phase 4 wire distribution system than the autotransformer must be directly connected to the ungrounded phase conductors and cannot have a switch or overcurrent  protection that is indendent of the main per 450.5 A(1)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources