Inverter earth fault
Inverter earth fault
(OP)
Hi to all. I have noticed some tripping of a Danfoss inverter VLT5000 with alarm 14 EARTH FAULT. After recycling the power and resetting the inverter it resumes normal operation. Is there any logical explanation for this ? Earth fault is a short circuit between phase and earth and is something more or less permanent. Should i suspect the screnned cable between inverter and motor or should i expect a possible motor insulation failure ?
Thanks in advance for your time.
Thanks in advance for your time.





RE: Inverter earth fault
RE: Inverter earth fault
If you do have the grounding in place, an intermittent motor insulation failure is probably the most likely cause. Usually, it just gets worse until the motor fails. In the meantime, most drives have a provision for turning this fault off. You may want to do that to avoid the nuisance.
If your power supply to the inverter is one of those nasty floating delta or high resistance grounded wye systems, the drive will often confuse imbalance problems on the supply for motor lead grounds. Your only recourse in that case is to turn the fault off in the software.
Don't you just love those floating networks!!!
RE: Inverter earth fault
"Our virtues and our failings are inseparable, like force and matter. When they separate, man is no more." Nikola Tesla
Member, P3
aarthoogerwerf (Electrical)
one question first: Do you have a long motor cable or a cable type with high capacitance. This can cause earth fault trips.
alexit (Mechanical)
How long has the system been operating? Is this the first problem with motor/drive system? If yes, its time to start testing. Lets say your system was working fine for 6 months:
Read the Eng-Tips Site Policies at FAQ731-376
RE: Inverter earth fault
Also some motors have very high capacitance to earth, because of their construction.
You can measure this (disconnect cable from converter)with an appropiate measuring instrument.
Check for allowed cable length in danfoss documents.
RE: Inverter earth fault
The VLT software will provide the same error for detected line to ground shorts and load to ground shorts. It can also supply this error in the event that your line earth is changing impediance.
Start with the motor, use a motor winding analyzer and be sure to measure loaded turn to turn and turn to ground impediance for each winding do this including any connectors used. Surge test at the repeatable hi-pot voltage, do this only twice per turn.
Now check the cable, you can bridge the ends at the motor connector and use the winding analyzer if this is a long run...otherwise just replace the cable with something acceptable for your motor. Be sure this cable is rated for the controller frequency of your VLT5000, this is usually 6-10kHz but somtimes up to 24kHz (I like the olflex products from Lapp.)
Does the system have an inductor or transformer between drive and motor? Check this with the winding analyzer too.
Now check line to the drive, does this have a inductor or transformer. Test it. Check the earth ground impediance, does this change when the machinery is running? When OTHER machinery is running? Now with everything running scope the input voltage/current waveforms from the mains, record for a week or so...is your local utility "helping" by playing with the voltage during peak hours? Does other machinery cause a spike during startup/shutdown? Be sure to check phase to phase synchronus error, is this less than 3%? Is it even close to 3%?
IF you still cannot find a reason, perform EMF "electrosmog" analysis...is the TV station satellite broadcast farm next door properly grounded? How about the airport weather radar sitting 300' from your parking lot? Are you located under imbalanced 1200kV high tension lines?
There is a reason for your error message, it means something is wrong...