Instruments in a CL I DIV II GRP C and D

Instruments in a CL I DIV II GRP C and D

Instruments in a CL I DIV II GRP C and D

(OP)
I am installing instruments in a Class I Div II area. The instruments are classified for this area. do i need to seal the electrical connection to these instruments, what other provisions do I need tokep in mind when I wire these instruments. Where can I get good information on instrument installation in classified area.

RE: Instruments in a CL I DIV II GRP C and D

We previously used safety barriers in a petroleum refinery, they acts as a isolation unit if there is excess capacitance or inductance.

You would also have to use spesifications on your instruments to do calculations of the capacitance and inductanse.

The instrument should be classified for your zone requirements. Idealy your source should be in a safe area with your barrier leading out to your zone area.

If i remember correctly you must also use Ex rated glands

Here is a good link describing the basics.

http://www.am.pepperl-fuchs.com/techresources/pdf/IS_in_a_nutshell-InTech-Dec2002.pdf


REMEMBER THAT YOU MUST CERTIFY THESE LOOPS with a certified explosion prevention authority

Hope it Helps

Regards

RE: Instruments in a CL I DIV II GRP C and D

501.15(B)(1) in the 2005 NEC only requires a seal at this instrument if the instrument is required to be in an explosion proof enclosure.  Per the exception to 501.105(B)(2) most electronic instruments do not require an explosion proof enclosure.  The 2002 code sections are 501.5(B)(1) and 501.3(B)(2) respectively.
Don

RE: Instruments in a CL I DIV II GRP C and D

Aren't seals are required where conduits travel from classified locations to general purpose areas?  The NEC (NFPA 70) is a complex assembly of rules and exceptions to the rules.

Read Article 500 through 505 of the National Electrical Code.  (Notice that the Class is a Roman Numeral and the Division is what we call an Arabic number, thus Class I Division 2.)  Allow some time to digest this stuff.

John

RE: Instruments in a CL I DIV II GRP C and D

If it's an IS instrument and you connect to it using the blue IS data cable which is a solid construction ie all airgaps filled with a gel or some other form of packer and there is an intrinsically safe barrier in the circuit in the safe area, and the callculations have been performed to determine that the cable length is ok, and you leave the safe area through a transit frame then you do not need a barrier. You really need to specify the details of the instrument,what zones you pass through etc. If you use conduit you should use barrier glands when transversing different areas.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources