design of busbars
design of busbars
Please design a copper bus bar system for an enclosure of 2 x 1.8 x 1 mtr. The current rating of the bus is 7000 A rms at 415 V for 180 secs. Thereafter the current is 1600 A rms continuous at the same voltage.
While 7000 A is being passed the bus bar should be within permissible temperature limite. The temp permitted at 1600 A is 80 deg C. (40 + ambient 40)
I only need to know the cross section of conductor needed. No other details are required.
Exact calculation is required.
Hari Haran Rajgopal
Hari Haran Rajgopal
RE: design of busbars
I might suggest that you pose this question on the Electrical Power Engineering it seems more like their sort of question.
Any help ?, yes no let me know.
anyway, you can use 1 sq. inch of copper carries 1000 amps..
..the resistivity of a pure copper is ...10.2 at 32 degF ..also,
this might help too..
Area of a circle = 0.785(dxd) cir mils where d is the diameter in cir. mils
In square measure,
Area of cir mils = 0.785x1x1 =0.785 sq. mils
Cir mils =0.785d squared/ 0.785 = d squared
good luck
dydt
1. NEMA BU-1 Busways
2. NEMA BU-1.1 General Instruction for Proper Handling, Installation,
Operation, and Maintenance of Busways Rated 600 Volts or Less
3. UL Std 857 Electric Busways and Associated Fittings
4. ANSI/IEEE C37.20 Switchgear Assemblies Including Metal-Enclosed Bus
5. ANSI/IEEE C37.23 IEEE Standard for Metal-Enclosed Bus and Calculating Losses in Isolated-Phase Bus
6. ANSI/NFPA 70 National Electrical Code
7. Visit
http://busbar.copper.org/ampacity/busbar.htm
8. Search this Forum. There are some excellent postings already