Ampacity Ratings of Urd Power Cable

Ampacity Ratings of Urd Power Cable

Ampacity Ratings of Urd Power Cable

(OP)
In trying to determing the ratings of underground cable for my company I determined that the manufacturers vary widely in their ratings, i.e., for 25kV 4/0 Copper 1/3 neutral 260 Mil insulated cable buried in ducts: Southwire = 287 Amps, King Wire = 320 Amps, and Perreli = 314 Amps. The ratings are all for 90 DegC, continuous current, in ducts.

My questions are:
1. Does anyone know why they vary so widely?

2.Which one is correct or is there a better document or calculation to get accurate ampacities?

Thanks.

RE: Ampacity Ratings of Urd Power Cable

(OP)
Correction, Rated at continuous current @ 90 DegF

RE: Ampacity Ratings of Urd Power Cable

Do the companies give details of the ducting used, if this is with or without bentonite filling etc?
I've seen some cable data that provides ducted thermal ratings but is based on 3 single core cables laid in trefoil in a single duct where as others can be based upon single core cables in seperate ducts.

This is the only thing I can think of other than the construction of the cable varying between manufacturers and some applying different de-rating factors for the thermal resistivity of the specific materials used.

RE: Ampacity Ratings of Urd Power Cable

(OP)
Some were more specific than others, but for most of them it is one cable per duct. No filling was mentioned.

RE: Ampacity Ratings of Urd Power Cable

I guess the variation in ampacity depend on the overall cable thickness, insulating material characteristics and cable construction that may be different among manufacturers.

In addition, there are other external factor and operating conditions assumed for the ampacity calculation such as:
ambient soil temperature(typ 20 oC), depth of duct bank, max. conductor operating temperature, earth thermal resistance (RHO), concrete RHO, duct RHO, duct diameter/thickness, load factor, number of circuit in the duct bank, cable arrangement, grounding points: Single vs. multiple, etc.

RE: Ampacity Ratings of Urd Power Cable

I'd would ask someone at the local utility if you can.  Soil conditions can vary by area and seasonally.  Around here the cables are essentially in mud except August of every third year when they think they are in Arizona.  

RE: Ampacity Ratings of Urd Power Cable

Could you be looking at two different insulation types? XLP vs. EPR maybe.

RE: Ampacity Ratings of Urd Power Cable

(OP)
No. They are all XLPE.

Thanks.

RE: Ampacity Ratings of Urd Power Cable

The companies that sell the cable should all have computer programs that can calculate allowable currents for your particular installation.  They are based on the duct configuration, depth of burial, earth ambient temp, load factor, wether the shield/neutral is connected at one end or both, what the earth thermal resistivity is (big factor but most people just use the standard Rho=90).  I would discuss this all with your cable manufacturer - you can contact Okonite (epr insulated cable - all we use) and they have an engineering data bulletin #ehb-98 that gives a lot of info on this subject along with tables of ampacity data for different configurations.  

One factor that makes a big difference is the earth thermal resistivity.  It varies with soil moisture, so just checking it at one point in time is not good.  We don't measure it here (we are a small cooperative) and I think most people dont bother to try to measure it, but it can make a big difference in the allowable ampacity. This is obovious if you think about it as the earth carries away the heat generated.

Also, your cable is probably rated at 90 degrees C

K2ofKeyLargo

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources