ME needs EE help

ME needs EE help

ME needs EE help

(OP)
Being an ME, I need some EE help. Can I reliably run one of those new tankless water heaters (essentially a big resistor), which draws 30A at 240Vac, from a 240Vac, 30A, 3 phase supply? Or will I be constantly tripping power?

Thanks,
Tim

RE: ME needs EE help

Probably..  A few more details would be helpful.  Is the 3Ph supply nothing special like a generator?  Is the waterheater 3ph? You didn't specify.

RE: ME needs EE help

(OP)
The supply is from our company's electrical distribution, so I suspect it's ultimately the local utility company. I think the heater is single phase. - Tim

RE: ME needs EE help

The NEC requires that the overcurrent protection for a water heater be sized at 125% of the water heater rating, so no, you can not feed a water heater that draws 30A from a 30A circuit.  The phasing and voltage of the supply circuit will need to match the water heater.

RE: ME needs EE help

(OP)
Thank you for your help. I'll consider alternatives. - Tim

RE: ME needs EE help

If the question is can a single phase load be served from a 3 phase supply, the answer is yes. To meet Code you will require a 40A, 2 pole breaker for a 30A, 240V rated heater.

I cant imagine your supply capacity is limited to 30A.

RE: ME needs EE help

Not sure about your application, but experience has shown that these babies are capable of producing some very noticeable lamp flicker when they kick in due to voltage dip.  Don't say I didn't warn you


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources