Communication problem

Communication problem

Communication problem

(OP)
Hi

We have one SLC500 plc controlling the essential functions of a turbine driven generator. The PLC communicates with our Woodward 505 governor through modbus protocol via a prosoft communication card. We had since the last three months two communication failure with the woodward governor and we had to remove power to the SLC500 to resume back communication.
Grateful to have some inputs from forum members.

Bob

RE: Communication problem

hi,

Is this link wired with a cork resistor (typical value 100 ... 150 ohms) to enhance "resistance" to emc disturbances ?
it shall be first point to check. according to my own experience, it fix such issue 8 times out of 10.

rgds.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources