Generator Decrement Curve

Generator Decrement Curve

Generator Decrement Curve

(OP)
I'm trying to determine if the inrush of transformers totaling approximately 5MVA of varying size XFMRs would damage or significantly be out of the range of performance of (2) 1875kVA, 0.8PF standby diesel generators.  
The transformers are significantly underloaded, but the connected load to the XFMR will have no real effect on the inrush that the gens will see during a open transition with application of full load.
Is it a fair assumption to say that the generators can handle approximately 15-16 times its full load current during transformer inrush, or will the voltage drop significantly to accommodate the 0.1 second inrush load?
I do not have decrement curves for the existing generators, but looking at some "typical" ones, it seems close.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources