Switchgear Maintenance
What is the standard and referrence for existing panelboard and switchgear electrical testing & maintenance? What is the desired interval for this maintenance? I have searched Manufacturers, NFPA, NEC, Nema and found little instruction yet, I am certain there must be an authority with multiple written sources of information on the subject.
RE: Switchgear Maintenance
the bible to testing specifications is most definatley NETA (international electrical testing association)
They have 2 books that tell you how to test everything.
the two books I go buy are the "Acceptance Testing Specifications" - for brand  new equipment
"Maintenance Testing Specifications"- routine testing on existing equipment
The typical standard for maintance is once every 1-2 years.
Also, from the NETA standard, depending on the reliability of the system and it's age/condition will also determine frequency of maintenance.
              Poor           Ave.         Good
Low             1             2            2.5
Med             .5            1            1.5
High            .25           .5           .75
The numbers in the columns are the multiplication factors to apply to typical maintenance frequencies.
This is from the 2001 NETA standard.
Mike
ted - look at NFPA 70
Jimi