I am doing a project that invloves using an NGR and I have to size the cable to it.

The system is 1MVA, 25KV step down to 4160V. From the transformer we're connecting to 4160V switchgear (benshaw controllers on them) to feed 2 - 800HP motors.

Can anyone point me in the right direction for this? I haven't dealt with NGR's since school.

Thanks

RE: Sizing cable to NGR

Determine the resistor rating, both in ohms and fault current.  Rating is probably given as amps over time such as 400A for 10 seconds, 200 amps for 1 minute, or 100 amps continuous. (Se IEEE Std 32.)

Size cable for the fault current.  You could save some cost by sizing the cable for the continuous rating only and verify the short time rating (See IEEE Buff Book). But the cable will be so short that the cost difference is nothing.  IMO Size for the short time current.

Run 5 kV cable from the transformer neutral to the resistor and bare or 600V cable from the resistor to ground.

Resistor rating is determined by the protective relaying.  How long will a ground fault last before the protection clears the fault?

RE: Sizing cable to NGR

(OP)
Drawings list it going through a 200:5 CT, with a 25A CONT rating.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources