calculating minimum air gap
Mechanical engineer here, so sorry if this is a an easy question, or in the wrong forum. I need to determine the minimum air gap between two voltage carrying terminals, in order to prevent arcing. The terminals are parallel, with no protruding shapes in the direction of the other terminal. The circuit voltage is 14v dc with very low current Assume the nominal air condition is low humidity and high temperature (>130 degrees C). Hope this is enough information. Thanks
RE: calculating minimum air gap
Is this on a board?
Why are there no design standards for you to use?
Can't imagine being able to get terminals close enough to cause arcing without raising other concerns, e.g., the substrate bending and causing the terminals to short out altogether.
TTFN
TTFN
TTFN
Calculate what has to be calculated,
Don't calculate what don't have to be --or can't be --
calculated
and know the difference
--- OR ---
spend unlimited money and time.
<nbucska@pcperipherals DOT com> subj: eng-tips
read FAQ240-1032
you specify >130C but not the highest temp. IRstuff's rule is not valid for much higher (e.g. 500 C )...
To prove the previous rule of thumb:
A yound engineer once specified a $1500. -2V precision pover supply -- I changed the design to use a 10K 1/4W resistor to -15V which is less than a dime.
read FAQ240-1032
One day my ship will come in.
But with my luck, I'll be at the airport!
When simply considering likelihood of failure, there are significantly more and more probable possibilities than worrying about the 14V delta causing an arc across a relatively huge gap.
TTFN
Does this coil ever switch? If so (in absence of surge supression) there may be a voltage transient may be orders of magnitude higher than 14v.
identifies the minimum "sparking" potential for air is 327 volts.
Once again what it is saying is that at your voltage 14V (or any voltage below 320volts) in theory you could put your terminals one Angstrom apart and there will be no arcing.
Revised calculation 14v / [75kv/inch] is even more
outrageous 0.0002 inches.
Once again I am not proposing to use any of the above "theory" as a guide. Exactly the opposite.
I think if the gap is VERY small, the current can just tunnel through. There is a gap between the Cu atoms,
too...
read FAQ240-1032
This is especially true for breakdown voltages.
A rule of thumb is if the voltage is doubled, the gap is tripled.
Reference Data for Radio Engineers fifth edition page41-1 has Spark-gap breakdown voltages.
The lowest chart goes is 1000 volt peak For needle gap it is 0.025 inches at 25C, 29.9 inches of mercury.
The multiplication factor for 60C is 0.50
So breakdown for 0.025 inch gap at 60C is 500 volt peak.
Page 41-2 states "The breakdown voltage is approximately proportional to pressure and inversely proportional to absolute (degrees Kelvin) temperature"
If you are actually operating at 120C, I would suggest making some tests.
TTFN
But since it is the subject of this thread, why don't you tell us the factors that contributed to your arcing?
The gap can be narrowed by contamination. Was this a new
PCB or an old one ?
read FAQ240-1032
TTFN
Do you have an explanation for the arcing? Why did you call it badly designed?
Bad design for a number of reasons.
TTFN