Hi Everyone
We are facing a problem of moisture occurance in 33kV air insulated switchgear in the cable compartment.Is it ok to leave silica gel bag in the compartment to absorb moisture.
Thanks to answer the question.
Cheers
We are facing a problem of moisture occurance in 33kV air insulated switchgear in the cable compartment.Is it ok to leave silica gel bag in the compartment to absorb moisture.
Thanks to answer the question.
Cheers






RE: Moisture in Switchgear
Causes for moisture if it is a air conditioned room:
1. Air leaks from control cables entry- Arrest with foam seals
2. Negative pressure in the room - Adjust air return dampers.
Silica gel is not a solution for high moisture codensation. Instead space heaters are more preferrable. But I haven't seen any space heater in cable compartments of MV/HV switchgear.