1336 drive
1336 drive
1336 drive
Hi guys, We have been running a 20 h.p motor at 90HZ through a 1336 plus drive trying to find the optimum speed for one of our processes,the motor tolerated this for about 36 hours and then quit, the motor was a severe duty motor and the motor amps were correctly entered into the drives parameters.I would have thought the drive would have prevented motor failure by faulting out,but i have also heard that it is not advisable to run motors over base HZ because of harmonic problems and associated problems with bearing overheating. Could anyone advise if i am correct in my theories or shed some light on the problem please.
RE: 1336 drive
You don't really provide nearly enough information for a decent analysis, for instance the application, base motor speed, installation, motor failure description etc., but here are some generalities.
The problem with running a motor over base frequency is that the motor output torque is going to decrease at a logarithmic rate proportional to the overspeed, and if the load torque requirement is higher than that output torque, you are overloading the motor. For example if this was a centrifugal pump, the load power requirement will increase with flow, which increases with speed. So even if your motor was oversized by 20% at full speed, a 50% overspeed will have increased your power requirement by 50%, but your motor power remained fixed, meaning the motor was 30% overloaded (very rough math, but you can follow the idea). Most VFD's motor protection algorithms are sophisticated enough to provide protection in this circumstance, but I cannot attest to the 1336's ability, you would have to ask A-B.
You are correct to worry about the bearings, but to be honest most 20HP motors use common parts, so an 1800rpm motor uses the same bearings as a 3600rpm motor, so that may be irrelevant. If you have a 3600rpm motor that you were running at 5400rpm however, you may have in fact cooked the bearings. You need to check that out with the motor mfgr.
Harmonics are an issue regardless of overspeeding, so if your motor design was not meant for VFD operation, it would only be worse running overspeed. Severe Duty does not specifically mean suitability to VFD operation. In particular, did you consider the distance from the drive to the motor? There are many issues regarding that, and if you ignored them, the fact that it was overspeed was not necessarily the culprit.
Also, some motor cooling fan designs lose effectiveness above base speed, so that may contribute to premature failure. Again, check with the motor mfgr.
Those are but a few of the issues at hand. Have a motor shop analyze the mode of failure in the motor. Sometimes that can give you a way of narrowing down the possibilities.
"Our virtues and our failings are inseparable, like force and matter. When they separate, man is no more." Nikola Tesla
Read the Eng-Tips Site Policies at FAQ731-376
Member, P3
RE: 1336 drive
1mick1, it is highly unlikely that the overspeed caused your motor failure.  90Hz operation is done commonly without problems.
You state that motor nameplate parameters were correctly entered into drive.  But is the drive overload protection turned on?  If not, at 90Hz, overload occurs at 2/3 the torque rating of the motor at base speed and the drive would not protect the motor properly.  If the overload protection is turned on, the protection would be good.
Now look at the nameplate of the motor and check for Insulation Class.  If it is B, the motor would have failed due to inadequate insulation rating at any speed.  If it is Class F and the motor leads back to the drive are over 75 ft long, you also are having insulation problems unrelated to overspeed.  If you motor leads are longer than  75Hz, you may well need a reactor inbetween the drive and motor to clip out the high frequency components.  Your motor will last a lot longer.
Either way, have a good motor shop take a look at the motor.  They can tell you why it failed, usually.
RE: 1336 drive
I agree with Dick, the problem with the motor may be unrelated to the drive. Get the motor inspected by a good shop and get their comments first.