Looking For Large DC Rated Safety Switch
Is anyone using a high current DC rated safety switch to disconnect a battery bank from a load?  Operating conditions is 300 VDC and 265 Amps.
RE: Looking For Large DC Rated Safety Switch
If in the USA, Pringle is one manufacturer.
Now-ad-days DC circuit breakers manufacured by Square D are common in large UPS applications.
What do you mean by safety switch? There are a few suppliers of load-break switches for DC duty, but they are large and expensive. Please define requirements a bit more.
One day my ship will come in.
But with my luck, I'll be at the airport!
Most all of the major manufacturers offer this, but to get above 250VDC rating you need to look at the heavy duty 600V rated units. I just checked the Square-D catalog and they go up to 1200A @ 600VDC. Click here and then hit the "NEXT" button near the top-right of the page for 600VAC/DC
I'm sure that Siemens, Cutler Hammer, GE etc. all follow suit.
ScottyUK,
A "Safety Switch" is a specific design of disconnect swith here in the US. Knife blade, dead front, vertical handle operation, lockable in the Off position.
"Our virtues and our failings are inseparable, like force and matter. When they separate, man is no more." Nikola Tesla
Read the Eng-Tips Site Policies at FAQ731-376
Member, P3
Thanks for all your help.  The Square D product was exactly what I was looking for.
Thanks jraef - we're divided by a common language again! You guys need to learn English
NEWB - sorry for my ignorance!