Circuit Protection Calculation

Circuit Protection Calculation

Circuit Protection Calculation

(OP)
I have a 220V circuit board protected by a 75A breaker, I wish to install 2 new breakers, how do I work out if I need to up the 75A breaker?

RE: Circuit Protection Calculation

The best thing to do is to put a circuit monitoring device on all of the 3 phases, and let it record for 30 days, which I believe is an NEC requirement if you are in the US.  This will give you a baseline reading.  Then you can determine if your panelboard can handle the new load.

Mike

RE: Circuit Protection Calculation

I assume the 75A breaker is on the Incomer to the switchboard.
To determine if the existing 75A Incomer breaker is adequate for the propopsed increase in switchboard load :-
1.) Measure switchboard existing maximum demand current over 15 minute demand interval.
2.) Add to this max demand the max demand of the proposed new load.   Continuous rating of Incomer must be greater than max demand.
3.) Check that the proposed max demand does not exceed the continous rating of main busbar in the switchboard.
4.) Calculate max prospective 3 phase short-circuit current at the switchboard.  Interrupt rating of the breakers must be greater than the fault current.
Note: The breakers on the outgoing circuits can have interrupt rating less than prospective fault current only if the incomer and outgoing breakers are current limiting and chosen from the manufactuer's certified tables.
5.) Check grading is provided in the event of a fault downstream from the outgoing breakers.





Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources