Distribution Fuse Sizing

Distribution Fuse Sizing

Distribution Fuse Sizing

(OP)
What is the common practice for sizing fuses on a 4.16/2.4 multi-grounded distribution ckt in terms of connected kVA/load?  For example, the connected kVA on a ckt is 145 kVA (60 A) while the minimum SLG fault current is 915 A.  The fault current is for a bolted fault, so for coordination I am assuming 67% fault current.

Thanks in advance

RE: Distribution Fuse Sizing

Maximum fuse size will be in your local electrical code.  Minimum size can be what you want it to be, except if the fuse is too small it may nuisance blow or simply overheat.  You mention coordination, general approach is to start at the last device and work back toward the primary, without exceeding the maximum ampacity for each device allowed by code.  Where do you get using 67% of the fault current for coordination?  Primary fuse on a secondary L-G fault through a delta-wye transformer sees only 57.7% of the fault current, and on a secondary L-L fault through a delta-wye transformer sees 115% of the fault current.  On solidly-grounded wye systems L-G fault current can be up to 125% of the bolted three-phase fault current.  67% is a new one for me.

In your case you have to consider other variables beside connected load, including cable ampacity and inrush current of your largest load and whether it could be the last load energized.  Example: start with largest motor, determine locked rotor current above which your motor circuit protector has to be set.  The fuse must lie above and to the right of the motor circuit protector curve up to the maximum fault current available for complete coordination, without exceeding the maximum size allowed by code.  However, if the motor is started last, you have to add the inrush to the existing load current and leave more margin for the fuse.  Sometimes coordination and/or protection has to be sacrificed, making this more art than science.  Check out ANSI/IEEE Std 242 (Buff Book) for more info.

RE: Distribution Fuse Sizing

(OP)
Redtrumpet,
Sorry, I guess I didn't explain myself well enough.  These are cutout fuse links on an overhead utility distribution system.  Therefore the NEC and Buff book aren't that useful.  
What I'm trying to find out is what is an acceptable percentage of connected load for fuse sizing?  For instance, I know on one side tap on my system, the connected load is 90 A and a 40K fuse link works fine.  Obviously, all 90A is not being used.  For a 40K link, without taking into account pre-loading, ambient temperature, the melting time for 90A is 100 sec.
The 67% is an attempt to take into account a non-bolted fault, such as a tree limb or downed power line where fault current may look like an overload.

RE: Distribution Fuse Sizing

Thanks for the clarification - you can probably guess I am not a utility guy.  This is outside of my experience so hopefully somebody else can help you.

RE: Distribution Fuse Sizing

One Electric Utility's practice is as follows:

(1) assume a 60% diversity factor
(2) do not load K link fuses beyond 60% or T links beyond 75% of its rating

for 4 kV this

    connected kVA            kVA
20K     50           12T     40
25K     60           15T     45
30K     75           20T     60
40K     95           25T     75
50K    120           30T     90
60K    160           40T    120
80K    190           50T    150
100K   235           65T    195

Hope this helps

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources