Sizing economiser safety valves

Sizing economiser safety valves

(OP)
I am sizing economiser safety valves using ASME Section I, clause PG-67.2.6 and seem to get different capacities if I use the US customary unit and the metric method.

For example, the maximum heat absorption of the economiser is 15.8MW which I convert to 53.9 million BTU/h. (Conversion factor is W * 3.412 = BTU/h)

Using the US unit method, the required capacity is BTU/h divided by 1000 which is 53900lh/h which I convert to 24450kg/h. (Conversion factor is lbs * 0.45359 = kg)

Using the metric method, the required capacity is W divided by 1.6, which is 9.9 million kg/h which converts to 21.8 million lb/h. (Conversion factor is kg * 2.2046 = lb)

Any advise/comments would be welcome.

athomas236

RE: Sizing economiser safety valves

15.8 mw = 5.395983 e 13 BTU/hr
Using your 1000BTU/LB conversion which would be close >IF BOILING OCCURS IN THE ECONOMISER< , that gives you 5.396e10 Lb/H steam flow.=  2.4476 e 10 kg/h

RE: Sizing economiser safety valves

(OP)
Jim,

Could you check your conversion from MW to BTU/h I get 5.39E7 not E13.

Also the conversion you mention is not mine but from the ASME code.

athomas236

RE: Sizing economiser safety valves

I did my conversion using "convert.exe" which is freeware gleaned from the web.  
MARKS' HANDBOOK shows 1 btu/hr=0.2928W
so 1 W=(1 BTU/hr /.2928 )=3.412 BTU/Hr
15.8MW=5.39 x 10e7 BTU/Hr.  
So I apologize and agree with you there.  

I still don't think you are boiling in the economiser, so the 1000 btu/lb (which is the vaporization energy of water), would not apply unless you are.  If you are calling an economiser what I have seen others call a Heat Recovery Steam Generator (HRSG), then boiling would definitely occur.  I am accustomed to thinking of an economiser as a heat exchanger that runs feedwater through the exhaust gas stack of a boiler.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources