Emergency Generator

Emergency Generator

Emergency Generator

(OP)
Hello.  I am working on a design review of the of a 50kw three phase gas fired emergency generator. I have the following configuration.

50kw,277/480V 3phase(Generator)->200A Automatic transfer switch->100A 277/480V Emergency Panel->30Kva Stepdown Xfmer-> 100A 120/208V  2nd Emergency Panel.

1200A MDP with 400A 3pole breaker->200A Automatic transfer switch.

I read in an article on the web that since the load on the emergency panels are 200A combined high and low voltage. That you can get maximum output by putting a 400A on the MDP panel. I was wondering does this make sense to do it this way or is it correct to have breaker to be same as Automatic transer switch rating or just the load of the initial panel?

RE: Emergency Generator

The breaker feeding the ATS should not have a higher rating than the ATS.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources