I have experienced two 33/11kV mal operations due to REF in the last two weeks due to external through faults. I'm checking the stability resistor settings and high impedance voltage settings. I saw a post for a spreadsheet that could make life easier, does anyone have a copy of this please ?






RE: Restricted Earth Fault Protection
Do a ratio test, a magnetizing test and a polarity test on each CT in the scheme and ensure they are correct. If the CTs are easily obtainable, it is actually very easy to test them.
I do have a home-made excel-sheet to do the calculations, it is not difficult to create it.
V max = I x (R ct + R wires)
where:
V max = max voltage
I = through fault current seen from secondary side of CT
R ct = internal resistance of CT
R wires = Largest value of lead resistance between relay and CT
If you have a stabilizing resistor
V setting = V max - (R resistor x i )
where
V setting = setting voltage
R resistor = Value of series resistor
i = operating current of relay