IDMT Relay
IDMT Relay
IDMT Relay
Is there an electronic replacement/alternative for the IDMT relay? It has been quite some time since I worked in the industry but I was told that the good-old IDMT has been virtually shelved on new or refurbed protection schemes.
Lyledunn
RE: IDMT Relay
I have just perused a number of web sites relating to this issue. Perhaps I should have done this first off! My question is thus answered. Thanks any way!
Lyledunn
RE: IDMT Relay
Yes, there are a lot of manufacturers who manufacture IDMT-relays.
This new relays can do much more than the old elctromechanical relays - You can choose different curves,  do metering, see fault data, have much lower burdens, do self testing, etc, etc. Some manufacturers are ABB, Reyrolle, SEL, Siemens, Strike, GE, just to name a few.
Some of the disadvantages of the modern relays are:
Can't see the disc turning
Must have some kind of power supply
Can't do series tripping (where you use the CTs to supply the tripcoil during a trip)
But, the advantages of the new relays are much more than the few disadvantages.
RE: IDMT Relay
IDMT is a characteristic based on the fault current and operating time. All the latest Numerical and digital relays have the same charateristics in built. Well  the new realys have the wide range of settings , so that it can be used for all over current applications. IDMT relays , in electromagnetic version has three different relays for different characteristics\viz normal, very inverse and extremely inverse.
The lateastrelayshave all these three modes inbuilt in one relay cabinet itself.
RE: IDMT Relay
the characteristic of idmt "cdg 34"
RE: IDMT Relay
samchoy97
Please start a new thread when you are asking questions not relevant to the original question.
The CDG34 has an extremely inverse curve.
http://www.areva-td.com/static/largefiles/CDG14_UK.pdf
An approximate equation (IEC extremely inverse curve)
t = 80 x k / [((I-fault/I-set)^2)-1]
where:
t = time in seconds
k = time multiplier
I-fault = Fault current
I-set = Current setting