Transfer fans usage in commercial bldg

Transfer fans usage in commercial bldg

Transfer fans usage in commercial bldg

(OP)
I am reviewing a project design that utilizes a transfer fan.  It will be located in ceiling of one office room and using grills and ducts, transfer cooler air into a conference room adjacent to orignating room.  There are no fire walls, separations, or smoke separations involved.
I have looked through ASHRAE but have found no clear example, most quote exhaust fans for kitchens, bathrooms etc.

Another project just has a straight fan installed in wall of office, drawing in cooler air from main office.  Is this allowed?

Any info on allowed usage of transfer fans would be appreciated.

RE: Transfer fans usage in commercial bldg

If you are asking if using these sorts of fans are allowed...the place to look is your City mechanical code.

Transfer fans are quite common here in Los Angeles, especially under Tenant Improvement work taht involves with break rooms and dining areas. We normally use a transfer boots when its from room to room.

I dont know if that made any sense....

RE: Transfer fans usage in commercial bldg

HI, I don't think it is an efficient way to cool an adjacent room.  Especially since you have no issues with fire walls.  The only possible reason would be if there is not enough static pressure in the duct to push the air into the room.  This what fan powered VAV boxes are for. Consider the added cost of the fan, wiring, controls, and a short piece of duct and 2 grilles. Also the noise that people in the office and conference room would have to contend with.  
By placing a fan in the airstream, you will be adding heat to the air, lowering the cooling capacity.  Transfer grilles and ducts are common for return air applications in a ceiling plenum, because the air is warm and you do not have to worry about the throw of the air from a register.  It would seem to be allowed, just cheap.  These types of wall fans are usually relegated to machine rooms.  I recall an elevator machine room that had a thru-wall exhaust fan to the outside and a fire rated louver in the door to pull air from the hallway.
Try to duct it directly, sheet metal isn't as expensive as it was last year.
Dan

RE: Transfer fans usage in commercial bldg

Are you sure the fan isn't exhausting from the conference room?  We have a common practice of providing an exhaust fan with a speed switch for conference and meeting rooms.  It can be used by occupants if they feel it is getting stuffy in the space, or if someone has a strong perfume on the odours can be dissipated more readily.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources