First off, thatns for all the excellent advice on other threads. (You know who you are!)

We are using a transformer in our installation to go 480Delta:208Y/120 to feed office loads and receptacles. My question is what use do I have for the 208Y power? can I run (some) 240V single phase loads by tapping leg to leg, or is the 208Y basically useless in this case?

RE: 208Y loads

480Delta:208Y/120 volts is a very commom installation. You generally use it for your 120 volt requirements. No you can not get 240 volts. You must use 208 volt equipment in this installation. You need to spec the office equipment to use 208 volts. Most pieces of equipment will say on the name plate if it can be used with 208 volts.

RE: 208Y loads

(OP)
right, I know some (but not all) equipment designed for 240 also runs on 208. but it is wired leg-to-leg in single phase like I described, right?

RE: 208Y loads

Yes. But you just get 208V.

RE: 208Y loads

(OP)
methinks its easier to balance the loads if i keep it strictly 120V!

RE: 208Y loads

Well that isn't the only point!?  If the building has/needs A/C, or electric heat, or has an elevator, or electric water heater then you must make use of the higher voltage.

RE: 208Y loads

(OP)
yes, fortunately, we have none of those items!

RE: 208Y loads

Sometimes they do it on commercial buildings just because the transformer is smaller and cheaper, plus it makes the space more flexible for the next tennant.

"Our virtues and our failings are inseparable, like force and matter. When they separate, man is no more." Nikola Tesla

Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources