restroom/toilet ventilation
restroom/toilet ventilation
(OP)
As per Mechanical Code the for restrooms,the level of exhaust typically is 50 cfm per water closet or 2 cfm per square foot.
What is exhaust (cfm) of wash basin/lavatory?
In case if cooling is required, how to size the supply cfm of the restroom ?
What is exhaust (cfm) of wash basin/lavatory?
In case if cooling is required, how to size the supply cfm of the restroom ?





RE: restroom/toilet ventilation
Supply air CFM = effective room sensible heat/(1.08*dt)
dt = room design temp (Deg.F)-lvg. coil db temp (Deg.F)
sensible heat in BTUH
RE: restroom/toilet ventilation
RE: restroom/toilet ventilation
regarding the required exhaust cfm for wash basin/lavatory, for the reason of removal of humidity is there any fixed exhaust rate? I think 2 CFM/SQ.Ft.is not enough espically in humid weather.
RE: restroom/toilet ventilation