I was at a site earlier and was looking at the existing heating water plant for retro-fitting pneumatic controls to DDC.
There are 2 3-pass firetube boilers, 40 yrs old (defunct mfr), retubed and w/ newly installed burners. Prob 100 hp or so. No water treatment to be found.
No backflow preventer on the cw makeup either.
Anyway, the boilers are piped reverse ..... return into the top and supply out the bottom. Somebody put new valves on the pipes and did some modifications.
There is this ITEM on the return pipe right before an elbow and valve at the top of the boiler. This is the return side. The item is about 18" long with horiz water connections and a bolted top. There are 2 pressure gauges on it. The tag says "Superior Combustion Thermal Protection Valve".
It looks similar to a Sarco FT450 super capacity F&T trap.
This is a HW system.
What is it?
There are 2 3-pass firetube boilers, 40 yrs old (defunct mfr), retubed and w/ newly installed burners. Prob 100 hp or so. No water treatment to be found.
No backflow preventer on the cw makeup either.
Anyway, the boilers are piped reverse ..... return into the top and supply out the bottom. Somebody put new valves on the pipes and did some modifications.
There is this ITEM on the return pipe right before an elbow and valve at the top of the boiler. This is the return side. The item is about 18" long with horiz water connections and a bolted top. There are 2 pressure gauges on it. The tag says "Superior Combustion Thermal Protection Valve".
It looks similar to a Sarco FT450 super capacity F&T trap.
This is a HW system.
What is it?





RE: Calling old-timers - stumped on valve
But it makes no sense to put such a thing in the return line...
Mike Halloran
Pembroke Pines, FL, USA
RE: Calling old-timers - stumped on valve
RE: Calling old-timers - stumped on valve
"The control logic for all four temperature control valves options is the same. The flow of supply water from the boiler is allowed to flow into the system provided the return sensor is above the setpoint, in this case 135F. The flow into the system from the "boiler envelope" will increase as the valve opens or the pump speed increases, provided the return sensor is satisfied. If the temperature in the return line decreases, the valve will continue to close to maintain a safe condition. In the case of the variable speed injection pump, the pump speed will decrease to maintain the same safe condition. Although this is a rather simple explanation, the control algorithms can be very sophisticated since satisfactory performance is expected".
h
RE: Calling old-timers - stumped on valve
The pumps are constant speed.