NFPA 13 Section 5-13.1.1 ex. 7

NFPA 13 Section 5-13.1.1 ex. 7

NFPA 13 Section 5-13.1.1 ex. 7

(OP)
What is the definition of a concealed space over an isolated small room. I have an attic with 2 hour wrap backs less than 55 square feet. Would it be possible to elminate sprinklers in these areas even though the attic is over a 6 plex apartment complex.

Thanks in advance

RE: NFPA 13 Section 5-13.1.1 ex. 7

if the room itself is under 55 sq feet. Do not understand you r question are you saying you have areas in the attic that are broken into areas less than 55 sq feet??????

RE: NFPA 13 Section 5-13.1.1 ex. 7

Also you do not say if you are doing a full 13 system or 13R. Check you may meet some of the other exceptions to concealed spaces.

RE: NFPA 13 Section 5-13.1.1 ex. 7

(OP)
Basically I have small areas ( less than 55 sq. ft.) in some areas around  2 hour seperation walls. Just little pockets that have been formed. It is a full 13 system.

RE: NFPA 13 Section 5-13.1.1 ex. 7

Check with the local Authority Having Jusidiction to be sure.

RE: NFPA 13 Section 5-13.1.1 ex. 7

so you should be sprinkling the attic with a full system and any concealed spaces that do not meet any of the exceptions. So look at the exceptions and sprinkle if you do not or make is so that you do meet the exception, such as stuffing insulation in the void, or making the area six inches or less, etc.

you do not indicate how you are involved in this general contrac, sprinkler contrac, etc????????????

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources