Electrostatic Shield Isolation Transformer Grounding
Do I need to take special consideration for ground and neutral connections on the secondary of a Electrostatic Shield Isolation Transformer?  Its a delta-wye 480 - 208/120.  I've heard that you bond the neutral and ground at the transformer...if so...How do I deal downstream with grounding the panel frame without creating a parrallel return path?  Many thanks for any help....reference to a wiring diagram would be great!
Thanks folks!
Sense
RE: Electrostatic Shield Isolation Transformer Grounding
Ground the transformer like any other. One neutral to ground bond, either at the transformer or at the panel. With only one neutral-ground connection, there are no parallel return paths.
The shield is typically bonded to the transformer frame.