Gents

I need to check some existing protection settings on an MWTU01 (5A relay) reverse power protection relay, I do not have the corresponding Alstom document and would appreciate some assistance.

The relay is used to prevent excess power export to the DNO (ie to ensure that the power export limit is not exceeded).

Plimit  = 2.64MW @ 11kV
CT      = 800/5
VT      = 11,000/11O

I = 2.64E6 / (1.732 * 11,000) * 5 / 800 = 0.866A

Therefore 0.866A / 5A * 100 17.3% (ie Pn% = 17.3)

I am informed that the esisting relay setting is 30% (the sheet indicates Pn = 317.5 W which I can make little sense of - see below). If I am correct is equivalent to a reverse power setting of;

5A * 30% * 800/5 * 1.732 * 11,000 = 4.57MW

This is in excess of the clients export limit / agreement.

-----------------------------------------------------------

Thanks




RE: MWTU Reverse Power Relay - Setting Advice

(OP)
Cheers Ralph

Doh, just sussed my error / oversight;

I am happy that I am correct now that I have seen the connection with the 317.5W (I had taken the value of the clients protection drawing as being the relay setting, whereas it is actually the relay rating - which becomes obvious when looking at the schematic for the MWTU 01).

The 317.5W does then make sense since it is a phase quantity, therefore;

3*317.5W * 800 / 5 * 11,000/110 = 15.24 MVA (ie = 800A)

& Pn% = 2.64 / 15.24 * 100 = 17.3% (ie same as previously calculated).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources