Apartment Bldg, 4-pipe fan coil
Apartment Bldg, 4-pipe fan coil
(OP)
Desiging a building with 1 and 2 bedroom units. Using Air cooled chillers and modular non-condensing boilers. Trying to select coil delta-T's for the chilled and hot water, just wanted to get some opinions. Planning to use 44F-56F chilled and was hoping to get 30F delta-T across the hot water coil, to minimize pumping requirments. Should I stick with 20 F? Any thoughts?
Thanks.
Thanks.





RE: Apartment Bldg, 4-pipe fan coil
RE: Apartment Bldg, 4-pipe fan coil
52 deg F - 42 deg F = 12 deg F
HVAC68
RE: Apartment Bldg, 4-pipe fan coil
56 deg F - 44 deg F = 12 deg F
HVAC68
RE: Apartment Bldg, 4-pipe fan coil
RE: Apartment Bldg, 4-pipe fan coil
RE: Apartment Bldg, 4-pipe fan coil