Apartment Bldg, 4-pipe fan coil

Apartment Bldg, 4-pipe fan coil

Apartment Bldg, 4-pipe fan coil

(OP)
Desiging a building with 1 and 2 bedroom units.  Using Air cooled chillers and modular non-condensing boilers.  Trying to select coil delta-T's for the chilled and hot water, just wanted to get some opinions. Planning to use 44F-56F chilled and was hoping to get 30F delta-T across the hot water coil, to minimize pumping requirments.  Should I stick with 20 F?  Any thoughts?

Thanks.

RE: Apartment Bldg, 4-pipe fan coil

30F can be ok with hot water coils but it is better if you compare the initial cost(as you require bigger coils) vs the running cost. Stick to 20F for chilled water.

RE: Apartment Bldg, 4-pipe fan coil

20 deg F seems to be very high for chilled water coil.  12degF is ok.  Higher delta T would mean lower flow, thereby cooling coil selection poses difficulties resulting in lower velocity and a laminar flow which affects heat transfer.  The problem get compounded during part load, since water flow would further go down.

52 deg F - 42 deg F = 12 deg F

HVAC68

RE: Apartment Bldg, 4-pipe fan coil

20 deg F seems to be very high for chilled water coil.  12degF is ok.  Higher delta T would mean lower flow, thereby cooling coil selection poses difficulties resulting in lower velocity and a laminar flow which affects heat transfer.  The problem get compounded during part load, since water flow would further go down.

56 deg F - 44 deg F = 12 deg F

HVAC68

RE: Apartment Bldg, 4-pipe fan coil

you will get better cooling coil performance with chws of 42

RE: Apartment Bldg, 4-pipe fan coil

That is a mistake from my side. When I said 20F for chilled water, I meant it is the difference between supply air and room condition but I mixed up things.

RE: Apartment Bldg, 4-pipe fan coil

With (4) pipe fan coils the most you can do is total 4 rows. That is 3 row chilled water, 1 row hot water or 2 row chilled water and 2 row hot water. Check fan coil performance but I think the most you can do is 10°F T rise on the chilled water & 20°G T rise on the heating water. Make sure you use two way control valves & central bypass valve to allow diversity and not run out of gpm.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources