MATHEMATICAL ANALYSIS OF WATER EFFECTS

MATHEMATICAL ANALYSIS OF WATER EFFECTS

MATHEMATICAL ANALYSIS OF WATER EFFECTS

(OP)
I am curious to see how we would mathematically treat the effects that water would have on current carrying conductors.

RE: MATHEMATICAL ANALYSIS OF WATER EFFECTS

Can you be more specific? Are you interested in quantifying unwanted conduction through insulating materials as a function of water content?  What type of insulating materials?  What type of equipment?

RE: MATHEMATICAL ANALYSIS OF WATER EFFECTS

(OP)
Exaclty. I was thinking of quantifying conduction through insulating materials as a function of water content also. Well, type of equipment would be say, 50HP motor with #2 AWG Cu cable, standard insulation. Was curious about the general train of thought involved, a detailed approach if possible.( couple of eqns etc.)

RE: MATHEMATICAL ANALYSIS OF WATER EFFECTS

Tough question.

For what it's worth, there is a graph of insulation resistance for one generator both dry and wet at:
http://www.usbr.gov/power/data/fist/fist3~1/3~1_f2.htm

For older thermoplastic organic insulation systems (asphaltic), the insulation itself absorbs moisture which affects the bulk conductivity... so you have to consider both volume-leakage and surface leakage.

For newer thermosetting synthetic insulation (epoxy and polyester resins) systems, moisture does not much absorb into the bulk of the insulation, and surface leakage would be the primary effect (although the presence of any surface leakage during a dc test depends on the presence of a weakness in the bulk winding at some point... perhaps scarf joints in end winding area).

Sorry, that's just my thoughts, and not much to go on. Anyone else?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources