Could someone please explain how a hi effieciency dx split system is designed? Does a 4 ton 10 seer remove the same amount of latent and sensible as a 4 ton 13 seer? Is the volume of air the same for both units (2000 cfm).If I am considering replaceing my 4 ton unit with a higher efficiency unit will I have humidity problems? I know higher efficiency means the same 4 tons cost less to operate, but what is the sacrifice or is there any?
Thank you
Thank you





RE: Hi effieciency dx units
Generally scroll compressors consume less power when compared to recips and most of the high EER(or SEER) units have these. Further, a 4 row coil condenser unit gives better performance at higher ambient temperatures and the compressor discharge pressures are lower when compared to a 2 row coil.
Happy Independence Day to all fellow Indians
RE: Hi effieciency dx units
RE: Hi effieciency dx units
RE: Hi effieciency dx units
Not so the evaporator side...Humidity is going to be effected, a large evaporator will operate at a higher suction with the same airflow, which without getting into copious detail will be accompanied by a lower dew point depression and that is largely the need in a HH A/C System
There are some who opt for 6-ton units on a 3-ton load...Effectively, the unit cycles such that it only operates 50% of the time even when its hot & humid...The interior space then goes from humid, to just a little less humid, and back to humid...And people then set the T-Stat for 64 so the damn thing has a chance to dry out the space.
And you SEER don't mean much if your unit is running 100% of the time and your living room is cold enough to age steaks...