Does anyone know the recommended industry standard for VFD motor contribution back to the system when performing a short circuit study?

RE: VFD Contribution to Short Circuit Study

I don't know if there is a standard, but obviously, worst case would be at full speed.  Typical induction motors are 6x fla.

Mike

RE: VFD Contribution to Short Circuit Study

(OP)
I had someone question whether I should be using the full contribution of the motor, or something less because there is a VFD involved.  Since the software I use doesn't allow for VFD modelling, the full contribution gets used.

RE: VFD Contribution to Short Circuit Study

If the VFD has bypass contactors, you need to account for full contribution.  If the VFD does not have bypass contactors, it it highly likely that there will not be any contribution.

RE: VFD Contribution to Short Circuit Study

(OP)
Are you aware of any standard or any place I can quote that would have me include or exclude VFD contribution from my study?

RE: VFD Contribution to Short Circuit Study

No, I know of no standard; but unless there are bypass capacitors or the VFD is a four quadrant VFD (capable of regenerative breaking) there is no path from the motor through the DC and back to the line AC.

RE: VFD Contribution to Short Circuit Study

(OP)
davidbeach,
In one email you mentioned bypass contactors and in one you said bypass capacitors.  Which do you mean?

RE: VFD Contribution to Short Circuit Study

I'm sure he meant contactors, there is no such term as bypass capacitors in VFDs. And I agree that a basic VFD has no path back to the line to allow contribution of motor regen during a fault. Look to see if your software desribes "power conversion equiment" or some such wording . Same issue. A power supply is not considered to contribute for the same reason. As far as coordination studies go, a VFD diode front end it just a power conversion unit. The motor on that VFD is considered to be fed from a "new" source on the load side of that power conversion unit.

Bypass contactors allow the possibility of the motor being connected to the line directly, therefore adding them back into the equation. Regenrative drives can also be thought of as contributors, but you get to add anyinductors (reactors or bus chokes) when considering it.

"Our virtues and our failings are inseparable, like force and matter. When they separate, man is no more."   
Nikola Tesla

RE: VFD Contribution to Short Circuit Study

Contactors; typing too fast, spell check doesn't do too well with correctly spelled wrong words.

RE: VFD Contribution to Short Circuit Study

Quote:

typing too fast, spell check doesn't do too well with correctly spelled wrong words.

How true.... especially correctly spelled wrong words.... and you see them first after you have pressed the "submit post" button

RE: VFD Contribution to Short Circuit Study

0.432ms after you hit the Send button to be precise, at least for me.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources