Air cooled condenser (R407C) - location

Air cooled condenser (R407C) - location

Air cooled condenser (R407C) - location

(OP)
What are the potential problem with locating air cooled condenser (R407C) bellow level of compressor and evaporator. Approximatelly 3m. I can see potential problems with pushing liquid out of the condenser, oil circulation and maybe flashing off gas? How can you avoid those problems? Thank you.

RE: Air cooled condenser (R407C) - location

This can be made to operate with appropriate control valves, and Parker Hannifin has a couple of arrangements in the Refrigerating Specialties application manuals about just this topic.  There is a minor penalty in that the control valves are not set to manage LOW head pressure as normal in a larger system but to manage pressure at All Times; and of course the HP liquid line pressure is always appreciably lower than the condensing pressure.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources