D-Walls in Water Charged Silty Sand
2

D-Walls in Water Charged Silty Sand

D-Walls in Water Charged Silty Sand

(OP)
Is there any experience out there in constructing diaphragm walls in silty sand with high groundwater levels.  I believe trench stability will be a problem.  Any comments?

RE: D-Walls in Water Charged Silty Sand

Dewater, dewater, dewater. Well points or a shallow well 16" and 10 feet below bottom of the wall.

RE: D-Walls in Water Charged Silty Sand

You must have the level of your drilling fluid ( bentonite mud or polymer mud ) at least 1.5 m above groundwater level to ensure stability of the excavation. This can be achieved with a backfilled working platform or surelaveted guide walls depending on what is practical. I would try to avoid dewatering as much as possible.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources