feeder sizing to demand?
feeder sizing to demand?
(OP)
I am in need of a clarification so...
If I use the demand load for things like kitchen equipment and receptacles do I get to use those discounts in sizing my feeders? or do I have to use 100% as in connected load when sizing the feeder? what about breaker sizing?
Thanks for any light that can be shed on this.
If I use the demand load for things like kitchen equipment and receptacles do I get to use those discounts in sizing my feeders? or do I have to use 100% as in connected load when sizing the feeder? what about breaker sizing?
Thanks for any light that can be shed on this.






RE: feeder sizing to demand?
RE: feeder sizing to demand?
Good luck
RE: feeder sizing to demand?
that give you any adjustments necessary. Table 220.3A,
220.11, 220.18, 220.19and 220.20. 220.30 allows an optional
caculation using the rules of the section.
The utility rules do not apply to your caculations.