Transformer 7.5 degrees phase-shift explained?

Transformer 7.5 degrees phase-shift explained?

Transformer 7.5 degrees phase-shift explained?

(OP)
Dear all,

I'm very familiar with phase-shift transformers supplying for instance large VFD- or other rectifier-loads. I totally understand how and why a phase-shift of 30dgs eliminates the 5th and 7th harmonic on the primary-side on for-instance a three-winding transformer. Of course, the same thing would also work if you have one Dy- and one Dd-transformer on the same network with approximately the same amount of current being drawn in both.

However, I've seen configurations with several three-winding transformers connected to a point of common coupling where the primaries are said to have a D+7,5dgs and D-7,5dgs. The 5th and 7th are efficiently eliminated on the primary side due to the 30dgs phase shift between the two secondary windings, and the clue is to obtain a so-called "pseudo 24-pulse system". I totally understand the theory behind the 15 degrees phase shift giving a 24-pulse system, and of course it is pseudo since it is only working well with balanced load on the different transformers.

So.... To the point, gentlemen; Can anyone give a good, practical explaination on what is being done in the transformer design to obtain a +7,5 or -7,5? I understand how 30 degrees is obtained with the Y/D, but I've never got a good answer on how the 7,5 occurs.


Br,
torslum

RE: Transformer 7.5 degrees phase-shift explained?

One way to obtain a phase shift is to have an additional secondary winding on each leg of the core. The main winding and then a smaller winding. The smaller winding is connected in series with the main winding of one of the other phases. For example,  the main winding on the A phase leg is connected to the smaller winding on the B phase leg. Since the B phase leg of the transformer is not in phase with the A phase leg it causes a phase shift.
 

RE: Transformer 7.5 degrees phase-shift explained?

Draw a delta and tap each winding at 87.6%. You get 7.5 degrees shift by my calculation. Any amount of shift is possible by this method.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources