Short Circuit Rating

Short Circuit Rating

Short Circuit Rating

(OP)
When we talk about SC rating of a piece of electrical equipment, such as switchboard, it is not quantified with a maximum allowable time duration.  However, when we apply the insulated power breakers in low voltage power distribution switchboard, those power breakers could withstand SC up to 0.5 or 1 second. Is it given that switchboards are constrcuted to withstand published SC level up to one or more seconds? I couldn't find anything on NEMA regarding this.  Thanks.

RE: Short Circuit Rating

The requirement for switchboards built to UL891 standards (most common in the U.S.) is 3 cycles.

RE: Short Circuit Rating

There is UL 1558 also for switchgear using ANSI rated breakers, which have a short time rating of 1 or 3 seconds...You need to look up those standards..Look up websites of reputed switchgear manufacturers.

RE: Short Circuit Rating

(OP)
Thanks for the helps.

RE: Short Circuit Rating

And power circuit breakers without instantaneous trip elements can only be used to protect UL1558 (aka ANSI) switchgear because of the difference in the bus bracing.

Molded case circuit breakers can be used to protect UL891 switchboards or UL1558 switchgear because they are required to have instantaneous trip.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources