Smart questions
Smart answers
Smart people
Join Eng-Tips Forums
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

canman (Civil/Environmental) (OP)
27 Jul 05 19:34
Does anyone know if NFPA states that newly constructed fire mains that serve sprinklered buildings or private on-site fire hydrants need to be disinfected (chlorinated) before put into service?  Case in point, I have 10 projects in Southern California that the contractor wants to know if he needs to disinfect on the private side of the double check detector device.  He has disinfected between the public water main up to the backflow device.  Thanks in advance!

Canman
stookeyfpe (Specifier/Regulator)
27 Jul 05 21:04
No such requirement exists in NFPA 24, which governs the installation of underground fire protection water mains.
TravisMack (Mechanical)
28 Jul 05 0:04
The only time this comes into play is when there is known conditions of MIC.

From NFPA 13, 2002:
15.1.5* Water Supply Treatment. Water supplies and environmental conditions shall be evaluated for the existence of microbes and conditions that contribute to microbiologically influenced corrosion (MIC). Where conditions are found that contribute to MIC, the owner(s) shall notify the sprinkler system developed to treat the system using one of the following methods:
(1)     Install a water pipe that will not be affected by the MIC microbes.
(2)     Treat all water that enters the system using an approved biocide.
(3)     Implement an approved plan for monitoring the interior conditions of the pipe at established time intervals and locations.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Back To Forum

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close