Calculate Phase current
Can anyone tell me how to calculate phase current on a DELTA
connected Transformer, Primary side?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Calculate Phase currentCalculate Phase current(OP)
connected Transformer, Primary side? Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
RE: Calculate Phase current
If you are talking about the current in each 'phase' winding of the transformer (internal to the transformer) then the current in each 'winding' arranged in delta would be the rated current divided by 1.732, at full load.
1.732 is square root of 3.
If you mean the current in each of the three conductor feeding the tranformer, it is the rated current of the unit at full load. This is also the line current.
At any other loads, the current in delta winding is line current divided by 1.732.
P = 3^0.5 x V line-line x I line
where:
P = Power rating of trsf in VA
3^0.5 = square root of 3
V = line to line voltage
I = Full load current
You can use this formula for either star or delta and on either side of the transformer.
For delta connection:
V line = V phase
I line = 3^0.5 x I phase
For star connection
V line = 3^0.5 x V phase
I line = I phase
Example
100kVA trsf, 11kV/380V delta primary /star secondary
Primary side
100 000 = 1.73 x 11000 x I line
I line = 5.249A
I line = 3^0.5 x I phase (delta connection)
5.249 = 1.73 x I phase
I phase = 3.03A
Secondary side:
100 000 = 1.73 x 380 x I line
I line = 151.934A
I line = I phase (star connection)
I phase = 151.934A