Specifying Anchor Rods
When you specify a straight anchor rod with the nut and washer at the end creating the "head", are there standard size washers that are typically called out?  For instance would you spec a 2x2x1/4, or 3x3x1/2 for instance?  Do we even specify washers if they are not needed by calculation, checking with the pullout strength Np in ACI 318 App. D?  I would like to use F1554 Gr. 36 straight rod instead of A307 hooked bolts.  Some of my columns will have a net uplift that isn't too large, but I would like to get it right for future reference also.
RE: Specifying Anchor Rods
Would you even need a washer?  Seems to me that aside from the thickness, the size of the nut alone is remarkably similar to the head of a headed bolt.
That's true, my inexperience shows with questions like this.  If the washer is not necessary would I just specify a double nut at the end, with a tack weld or somethign to hold the nuts on?
The plate washer is not really "necessary." it simply ensures you will develop your failure cone with out pullout, we specify a a plate washer(pl 3/8"X3"X3" w/ 3/4" dia anchors)  with a double nut on the end at all bracing/moment frame columns. we modify the embedment to get the proper cone. It just seams like good practice at places were there is uplift potential
I do the following.  I check that the nut has enough surface area for bearing per equation D-13, (ACI-02).  It almost always does.  Then I specify a single nut, tacked to the rod.  If I have a high fatigue application or I am nervous about the design then I typically specify like a 3/4" x 3" x 3" plate, tacked to the rod nut on the bottom side of the plate.  I got crazy one time when I was taking a yield line class in college and sized some of these plates, but I don't think it was ever warrented.  The nut alone will usually suffice in my opinion.
Thanks everyone, my boss would like to have a plate washer regardless so I'll use a 3x3 as suggested.  I appreciate the help.