Refrigerant Charge after Conversion

Refrigerant Charge after Conversion

Refrigerant Charge after Conversion

(OP)
In order to comply with the environmental people, I need to know the amount of refrigerant that is used to charge several centrifugal chillers.  The chillers are from the 60’s or 70’s.  I can find the amount of refrigerant originally used to charge the chillers, but they have all been converted to a non-CFC type refrigerant.  My question is, if a unit needed 1000 lbs. of R-12 will it need 1000 lbs. of HFC -134a.  If the conversion is not done on a mass basis, is it done on a volumetric basis or on the basis of cooling capacity?  I have the same question for R-114 to HFC-123.  If anyone can help it would be appreciated.

RE: Refrigerant Charge after Conversion

R-12
8. Charge with Suva® refrigerant. In general, the
refrigeration system will require less weight of
the Suva® 134a than of R-12. The optimum
charge will vary depending on the system design
and operating conditions. For most systems the
best charge size will be 75–90% by weight of
the original R-12 charge.
For best results:
• It is recommended that the system be initially
charged with about 75% by weight of the
original charge.
• Add the initial charge of Suva® refrigerant
to the high-pressure side of the system
(compressor not running) until the system
and cylinder pressures equalize. Then connect
to the low-pressure side of the system, start
the compressor, and load the remainder of the
refrigerant slowly to the suction side of the
system.
For entire article go to http://www.dupont.com/suva/na/usa/literature/pdf/
For R-11 or R114 with go here: http://www.dupont.com/suva/na/usa/literature/pdf/h42443_4.pdf

RE: Refrigerant Charge after Conversion

(OP)
Thanks for your help imok2

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources