I have a 12 lead 40 hp motor. They marked 2 leads as T3. I know there is a way to identify the leads with a battery but can not remember the procedure. Can anyone help?





RE: 12 lead 3 phase motor / lead identification
There were several good threads written about this proceedure, If you use advanced search option you will find a lot of good info.
Chuck
RE: 12 lead 3 phase motor / lead identification
T1 and T4
T2 and T5
T3 and T6
T7 and T10
T8 and T11
T9 and T12
If most of your terminals are identified try first continuity with any multimeter.
RE: 12 lead 3 phase motor / lead identification
Here is the excellent thread I remember reading this might be the proceedure your referring too. was not as easy to find as I thought.
Chuck
http://www.eng-tips.com/viewthread.cfm?qid=109107