Transformer overload
When ordering a drive isolation transformer should I specifically request the overload capability 150% for 60 sec, or this overload will be provided anyway based on some general standards transformer manufacturers must follow?
RE: Transformer overload
You get exactly what you specify. If you say 10 kVA - you get 10 kVA. If this is for a frequency inverter you should make sure that the bad power factor (not displacement PF but distortion PF) is taken in account.
A 50 percent overload (i.e. 150 percent load) for 60 seconds is not a problem for a reasonably sized transformer. It has a lot longer time constant - probably in the 15 minutes region, if naturally cooled. Forced cooling will make the time constant considerably lower and you may have a problem with 50%/60 secs overload. But not with a self-cooled one.
If the transformer manufacturer is any good, he will be able to help you out if you explain the application.
Gunnar Englund
www.gke.org